Connections for a water flow switch?
Posted: Fri Aug 02, 2019
HI. I have an RDC644XG controller in the laser cutter I'm building. I also have a water flow detection device which has a simple switch inside. Connection made when water is flowing.
I'd assumed I could just connect to the controller but having looked at the manual but now not so sure it's that simple. The diagram shows a water chiller with a 'water protect switch' two wire connection to the controller. The manual goes on to describe the connection thus:
"The input port of water protector for the first laser power source.
When the water protector 1 is enabled, the controller will detect
the input port of water protector 1. If this port is of low level, it
will be deemed normal; if this port is of high level, the controller
will forcibly close the laser to suspend the work in progress and
the system will warn. If the water protector 1 is not enabled, the
controller will not detect the input port of water protector 1 and so
the water protector 1 can be unconnected.
Water protection input must be 24V logic level."
So, can anyone confirm that I can't simply connect the switch across the terminals. What do I have to do - provide a switched 24v input when the water switch is closed??
I'd assumed I could just connect to the controller but having looked at the manual but now not so sure it's that simple. The diagram shows a water chiller with a 'water protect switch' two wire connection to the controller. The manual goes on to describe the connection thus:
"The input port of water protector for the first laser power source.
When the water protector 1 is enabled, the controller will detect
the input port of water protector 1. If this port is of low level, it
will be deemed normal; if this port is of high level, the controller
will forcibly close the laser to suspend the work in progress and
the system will warn. If the water protector 1 is not enabled, the
controller will not detect the input port of water protector 1 and so
the water protector 1 can be unconnected.
Water protection input must be 24V logic level."
So, can anyone confirm that I can't simply connect the switch across the terminals. What do I have to do - provide a switched 24v input when the water switch is closed??