Autofocus behavior
Posted: Sat Oct 09, 2021
				
				Hi everyone,
i have a question about my autofocus behavior (RDC6445GT5).
I have a Z bed with limit switch (NO) on top position which is wired to Z- limit input.
I installed the red pen type autofocus sensor (there is is a NPN NO inductive sensor inside).
As recommended i wired it in parallel to the Z- Limit.
Reset is enabled for X, Y and Z. This works as intended.
Z-Axis travel is limited to 250mm (Breadth)
After reset (homing) the Z table is on top position and i can move it down by 250mm before the controller limits further movement. -> Good
If i use autofocus on an object (i.e. 100mm), it touches the pen-sensor twice, lowers the table by the set focal distance (i.e. 10mm) and sets the Z coordinate to zero.
But after that operation the controller allows travel down by 250mm which would crash my machine. -> Dangerous
The travel should be limited to the remaining 140mm of travel (250mm -100mm -10mm = 140mm).
In user settings -> focus -> "focus sensor": ich can choose between "z limit" and "Probe".
Currently "z limit" is selected.
If i select "probe", the behavior is even more strange: Table moves up, touches probe or z-limit, moves down till i cancel the operation (i don't want to crash the bed). Even if i touch the probe by hand while the bed is moving down nothing happens.
Wiring the probe to "z+", it is not recognized by the controller. I even tried the "in1" which apparently has no function at all.
Is this a fault in my controller/firmware, or do you experience the same behavior with other controllers (6445g/s, 6442, others)
(for testing you should temporary limit the travel (breath) to a smaller value to prevent crashing your machine)
Btw. i have made pictures of the disassembled pen-probe. Maybe it is useful to someone.
			i have a question about my autofocus behavior (RDC6445GT5).
I have a Z bed with limit switch (NO) on top position which is wired to Z- limit input.
I installed the red pen type autofocus sensor (there is is a NPN NO inductive sensor inside).
As recommended i wired it in parallel to the Z- Limit.
Reset is enabled for X, Y and Z. This works as intended.
Z-Axis travel is limited to 250mm (Breadth)
After reset (homing) the Z table is on top position and i can move it down by 250mm before the controller limits further movement. -> Good
If i use autofocus on an object (i.e. 100mm), it touches the pen-sensor twice, lowers the table by the set focal distance (i.e. 10mm) and sets the Z coordinate to zero.
But after that operation the controller allows travel down by 250mm which would crash my machine. -> Dangerous
The travel should be limited to the remaining 140mm of travel (250mm -100mm -10mm = 140mm).
In user settings -> focus -> "focus sensor": ich can choose between "z limit" and "Probe".
Currently "z limit" is selected.
If i select "probe", the behavior is even more strange: Table moves up, touches probe or z-limit, moves down till i cancel the operation (i don't want to crash the bed). Even if i touch the probe by hand while the bed is moving down nothing happens.
Wiring the probe to "z+", it is not recognized by the controller. I even tried the "in1" which apparently has no function at all.
Is this a fault in my controller/firmware, or do you experience the same behavior with other controllers (6445g/s, 6442, others)
(for testing you should temporary limit the travel (breath) to a smaller value to prevent crashing your machine)
Btw. i have made pictures of the disassembled pen-probe. Maybe it is useful to someone.